If I have a tower or mast on the roof of my house, is it necessary to ground it ? There is about 20 feet distance to my station’s ground rod.
Thanks guy for the info provided.
But what about that if the ground wire from the roof is so long that it can act as as an unground and act as part of the antenna on the roof creating RFI issues ?
I have only had 1 setup like this, and ended up having to isolate my station power ground to eliminate the ground loop. Obviously bonding the power ground to the shack entrance ground would keep ground loops relatively short, I just wonder how a professional would do it.
With the station you describe with the sub panel, there are still ground loops when using a 3 wire plug and a station ground. Lifting the ground plug wouldn't float the ground because you have your station ground serving the same purpose.Professional:I for years avoided the tie between my station grounding system and the House Electrical ground system. I knew from experience it would be a noise generator. Yes it was, raised my threshold on some bands. I was able to reduce that increase in "ambient" noise threshold when I installed a tail cabinet in the shack.
I pulled a complete 60 amp 4 wire system to the shack.
I installed the panel where it was only about 5 feet from the outgoing 4/0 wielding cable that goes from bench to the first ground rod. I then connected the panel ground to that bonding jumper.
This dropped the the noise increase about 75%. I still get garbage from the washer/dryer about 20 ft. away, but it killed all the computer/TV and other appliance noise from the house.
I, like you was getting loops thru the normal house wiring, but most of the high level garbage was coming from all the 2 wire devices in the house.(lamps/tv's/computer supplies/Cell phone chargers) etc...
Thus having the shack as a separate 240/120 volt 60 amp/ 4 wire branch circuit that connects to my main panel which is only about 4 ft. from the main bonding electrode...
Helps a Bunch!!!!
338: Yes lifting the grounds, would be construed as an issue "Technically".
However the ground lifting adaptors, the better ones have a "tab" on them where you can attach a ground lead and run those back to your station ground.
This would help eliminate the "floating" equipment ground issue.
Again "Technically" not advised or recommended.
The real issue with those is if you have a device that has a 3 wire cord, and you lift and float that ground, you could experience a fault and suddenly you have a HOT Chassis/cabinet etc.
This may never be apparent to you, until you got between that device and your station ground!!!! Ouch!
Reminds me of the old days, where you don't touch the refrigerator and the stove at the same time! The simple fix back before the mandated 3 wire home branch circuit, was to "flip" one of those devices in the outlet.
Damn really showing my age now!!!!
All the Best
Gary
Is the ground you pulled for your subpanel the only bonding between your service panel ground and station ground rod?
I'm still curious about your noise reduction with the sub panel. Unless the noise was coming from appliances on the same circuit, I dont see a difference with the sub panel. All of your grounds are still tied together at the service entrance. Any noise on any ground (edit: or the neutral) in the entire house would still run to the service entrance, then back to your sub panel and into your station. At least that's how it seems to me. Any thoughts on this?Yes" #6 Copper fine strand about 35 ft long in Steel Conduit.
My station ground consists of 5 ground rods...First one like 6 feet from bench 4/0 wielding cable...2 more base of the tower/6 feet from first...then 1 more about 8 feet East and West from the tower...all connected with either 2/0 or 1/0 wielding cable using compression lugs.